Any plumbers / boiler engineers ??

Dellboy

Challenge Tour Pro
Joined
Oct 5, 2011
Messages
989
Location
Wilton, Nr Salisbury
Visit site
Hi,
Just wondering if we have any plumbers/boiler engineers here. I’m having a problem with our boiler. It’s a Worcester boiler (Greenstar 27cdi combi) and 3-4 years old, or so I’m told, only moved into the house 7 months ago.

Heating works fine, no problem with that; it’s the hot water, which is playing up.

Trying to take a shower is almost impossible, it takes a while to come through hot (due to boiler is at the other end of house), but then we only get 2-3 minutes (max) of hot water before it runs cold. So you have to run it again for another 4-5 minutes to get your next short burst of hot water.

It did work fine when we first moved it but has been getting worse. Had one chap round and told us we needed a new boiler, £1,100 + labor, a second chap said boiler was fine, must be the shower!! (Even though the same happens to the hot water in the kitchen)

I called Worcester; they said sounds like the Diverter valve and could send someone out to look but not for a while (not sure how long a while is?)
Now I did tell the last chap this info (diverter vave) but he said Combi boilers don’t have one.

So does anyone here know if I do have a Diverter valve with this boiler? And if so, does it sound like it would cause this fault?

I know it’s going to cost me, but so far I have not had much luck in sorting this and would just like an honest answer or advice.

Cheers

Dellboy
 

Pipetwister

Medal Winner
Joined
Aug 15, 2013
Messages
29
Location
Southampton
Visit site
This brings back memories!! Yes there is a divertor valve in the boiler and yes if it is sticking it will work ok in heating mode but no hot water. All combi boilers, unless they have a twin primary heat exchanger (Worcester i Junior) default to heating .
 

williamalex1

Money List Winner
Joined
Apr 7, 2012
Messages
13,445
Location
uddingston
Visit site
I asked my heating engineer mate , he said first thing he would try is the hot water sensor, which is cheap and easy to replace .

But remember to use someone thats gas safe registered.

PS , you do know that if another hot water tap is turned on while you're in the shower it will run cold for a while, maybe someones having a laugh.

I've been known to turn the downstair hot water tap on when the wifes in the upstairs shower[ by mistake of course] , you should hear the screams.:rofl:
 
Last edited:

Fish

Well-known member
Banned
Joined
Jun 25, 2012
Messages
18,384
Visit site
I think Qwerty is a plumber, or some kind of "engineer" where pipes, water, gas and solder may all come together :smirk:
 

Hogieefc

Club Champion
Joined
Jun 3, 2012
Messages
356
Location
Wirral
Visit site
Dellboy, is there an ECO button on the front panel, if its switched on turn it off and see if that makes any difference.
 
D

Deleted member 1740

Guest
Hi,
Just wondering if we have any plumbers/boiler engineers here. I’m having a problem with our boiler. It’s a Worcester boiler (Greenstar 27cdi combi) and 3-4 years old, or so I’m told, only moved into the house 7 months ago.

Heating works fine, no problem with that; it’s the hot water, which is playing up.

Trying to take a shower is almost impossible, it takes a while to come through hot (due to boiler is at the other end of house), but then we only get 2-3 minutes (max) of hot water before it runs cold. So you have to run it again for another 4-5 minutes to get your next short burst of hot water.

It did work fine when we first moved it but has been getting worse. Had one chap round and told us we needed a new boiler, £1,100 + labor, a second chap said boiler was fine, must be the shower!! (Even though the same happens to the hot water in the kitchen)

I called Worcester; they said sounds like the Diverter valve and could send someone out to look but not for a while (not sure how long a while is?)
Now I did tell the last chap this info (diverter vave) but he said Combi boilers don’t have one.

So does anyone here know if I do have a Diverter valve with this boiler? And if so, does it sound like it would cause this fault?

I know it’s going to cost me, but so far I have not had much luck in sorting this and would just like an honest answer or advice.

Cheers

Dellboy

Dell, It does sound like the diverter, when you run the hot water does your boiler lockout and need resetting manually?
 
D

Deleted member 1740

Guest
Not sure if you have the servicing manual for your boiler, it looks like a very simple job to change the diverter valve. Here is a link to your boiler manuals if you don't have them

http://www.plumbase.co.uk/documents/product/3550027

loook at page 49 of part 2 in the servicing manual and it tells you there how to change it.

Trust me, it isn't as simple as it looks.

I've been to planty of repair jobs where people have tried to change parts on their boiler because it looked easy enough only for them to call the expert because they've not done it properly.

Don't mess about with your boilers, get a expert in.
 

John_R7

Assistant Pro
Joined
Dec 1, 2012
Messages
123
Location
Central Scotland
Visit site
Google is your friend mate, the 2nd hit showed this...

https://uk.answers.yahoo.com/question/index?qid=20120107021108AAzewIx

Mentions the diverter valve as well, not sure what all that connecting the hose to the taps malarky is all about but I'd be giving it a shot, if nothing else then for comedy value :D

Didn't read all the link and don't have a combi.
We occasionally get air lock in the hot water and it will run slow (low pressure/volume) causig issue at the shower.
Have a mixer tap in the kitchen, block tap tightly with hand, open hot fully (can hold pressure back easily), open cold (from mains in mine) and the cold presurised water forces back along the hot water pipes and back to the tank. Close cold then hot.
Open hot where you are having issue (NOT on a mix). I open the bathroom wash hand basin as it is only hot and furthest from the supply. A minute or so and all the spluttering will stop - pipe full of water and ready to rock n' roll on our thermostatic mixer shower.

PS - hold on TIGHT to the mixer tap or it can have comic / rage value :lol:
 

Dellboy

Challenge Tour Pro
Joined
Oct 5, 2011
Messages
989
Location
Wilton, Nr Salisbury
Visit site
Google is your friend mate, the 2nd hit showed this...
https://uk.answers.yahoo.com/question/index?qid=20120107021108AAzewIx
Mentions the diverter valve as well, not sure what all that connecting the hose to the taps malarky is all about but I'd be giving it a shot, if nothing else then for comedy value :D

Got a mixer tap so could be a wee problem, but cheers mate.

I asked my heating engineer mate , he said first thing he would try is the hot water sensor, which is cheap and easy to replace .
But remember to use someone thats gas safe registered.
PS , you do know that if another hot water tap is turned on while you're in the shower it will run cold for a while, maybe someones having a laugh.
I've been known to turn the downstair hot water tap on when the wifes in the upstairs shower[ by mistake of course] , you should hear the screams.:rofl:

Hot water sensor, cheers, something else to check on, did run the hot once when wife was in the shower at my old house, she screamed as well, so did I when she got hold of me :eek:

Dellboy, is there an ECO button on the front panel, if its switched on turn it off and see if that makes any difference.

Gave the ECO button a try, didn't seem to make any difference, but cheers for that, I now know I have a ECO button :thup:

Dell, It does sound like the diverter, when you run the hot water does your boiler lockout and need resetting manually?

Never had the boiler lockout as of yet !

Not sure if you have the servicing manual for your boiler, it looks like a very simple job to change the diverter valve. Here is a link to your boiler manuals if you don't have them

http://www.plumbase.co.uk/documents/product/3550027

loook at page 49 of part 2 in the servicing manual and it tells you there how to change it.

Will have a look through cheers. Not 100% sure about touching a gas boiler, I know I could do it but not sure if I should do it, its a bit like me and my electrical work, I tell people to leave to the experts so I might have to sit this one out, but still a handy manual to have, cheers for that.

Didn't read all the link and don't have a combi.
We occasionally get air lock in the hot water and it will run slow (low pressure/volume) causig issue at the shower.
Have a mixer tap in the kitchen, block tap tightly with hand, open hot fully (can hold pressure back easily), open cold (from mains in mine) and the cold presurised water forces back along the hot water pipes and back to the tank. Close cold then hot.
Open hot where you are having issue (NOT on a mix). I open the bathroom wash hand basin as it is only hot and furthest from the supply. A minute or so and all the spluttering will stop - pipe full of water and ready to rock n' roll on our thermostatic mixer shower.

PS - hold on TIGHT to the mixer tap or it can have comic / rage value :lol:

Can see me getting a tad wet tiring that, not so sure its an air block more of a parts fail I'm thinking, but if the wife goes out I might give it a go :) :lol:

Cheers to all for the help, still tiring to work out my next move ??
 

MadAdey

Money List Winner
Joined
Nov 25, 2011
Messages
5,616
Location
Greensboro, North Carolina.
Visit site
Trust me, it isn't as simple as it looks.

I've been to planty of repair jobs where people have tried to change parts on their boiler because it looked easy enough only for them to call the expert because they've not done it properly.

Don't mess about with your boilers, get a expert in.

I suppose it depends how competent you are whe it comes to DIY. I changed out the heat exchanger and diverter valve on my combi boiler, but then I am pretty handy when it comes to things like this. But I would never touch anything on the boiler that involved the gas supply, I would leave that to the experts.
 
D

Deleted member 1740

Guest
Got a mixer tap so could be a wee problem, but cheers mate.



Hot water sensor, cheers, something else to check on, did run the hot once when wife was in the shower at my old house, she screamed as well, so did I when she got hold of me :eek:



Gave the ECO button a try, didn't seem to make any difference, but cheers for that, I now know I have a ECO button :thup:



Never had the boiler lockout as of yet !



Will have a look through cheers. Not 100% sure about touching a gas boiler, I know I could do it but not sure if I should do it, its a bit like me and my electrical work, I tell people to leave to the experts so I might have to sit this one out, but still a handy manual to have, cheers for that.



Can see me getting a tad wet tiring that, not so sure its an air block more of a parts fail I'm thinking, but if the wife goes out I might give it a go :) :lol:

Cheers to all for the help, still tiring to work out my next move ??

It's hard to diagnose without seeing it but I'd be looking at the DHW heat exchanger plate, that may be blocked rather than a faulty diverter.

Let us know if/when you get sorted.
 

Dellboy

Challenge Tour Pro
Joined
Oct 5, 2011
Messages
989
Location
Wilton, Nr Salisbury
Visit site
Update...

I now have lots of lovely hot water :thup: chap came round and worked out it was the heat exchange unit

So new unit cost me £127:00 and he charged me £75 for labour, while he was doing it he also gave the old boiler a service (The gas boiler, not the wife :whistle:)

Thanks for all your input chaps, Im off for a nice long shower.

Cheer

Dellboy
 
D

Deleted member 1740

Guest
Update...

I now have lots of lovely hot water :thup: chap came round and worked out it was the heat exchange unit

So new unit cost me £127:00 and he charged me £75 for labour, while he was doing it he also gave the old boiler a service (The gas boiler, not the wife :whistle:)

Thanks for all your input chaps, Im off for a nice long shower.

Cheer

Dellboy

As I suggested too :thup:.
 
D

Deleted member 1740

Guest
I hope you've got his mobile number now in you phone / written down / in a bank safety deposit box. He sounds a gud 'un. THEY ARE VERY HARD TO FIND !!!!!!!

I don't need to, I do it for a living!!
 